Brian Daly
I have 7 Ip cobalts on two modular boards and all was working fine.  Some are numbered for crossings and the point numbers are 101 - 105. I then added S lever control and for a time no issues. At a show a few weeks ago one crossing would randomly through even with no one at the board. I have checked all the connections and no stray wires. I have turned off self centring and re programmed the DCC address of all the crossings and no change. I Have disconnected all the levers to see if it was them that was causing it and no change. Checked the soldered connections for the plug to the s levers and cleaned them all up and no tracking. Advice needed?
Reply 0 0
m.bryan
Are the levers connected directly to the Digital IP via the PBS inputs - or via an AEU encoder?

If direct connection, how long are the wires from the lever to the motor?
(We have sometimes seen random operation with long wires on the PBS inputs - this is easily cured by putting a diode in series with wiring to the PBS terminals.)

If you are using digital operation via the AEU encoder - does the random operation occur with the levers disconnected form the AEU?

Regards,
Mick

Mick
Layout Concepts Tech/Customer support
Reply 0 0
Brian Daly
Wires are a max of 6 feet and yes wired direct. Which wire do you add a diode to? and which way?
Reply 0 0
m.bryan
Hi Brian,
Thanks for the info.
I've attached a diagram that shows connection of the diodes.
A simple 1N4001 type or similar will suffice


Hope this helps
Regards,
Mick
Mick
Layout Concepts Tech/Customer support
Reply 0 0
AHJAY
Another case where induction occurs.. Any pair of long, parallel wires to any digital device, especially if they are small. Twisting also helps here (Which is why all wiring for computers is twisted of course).

regards, Ahjay
Reply 0 0
Brian Daly
Sorry for the delay in posting a response. The diodes have worked for my problem. But any new wiring i will twist the wires as suggested and still add the diodes.


regards


Brian
Reply 0 0